Yesterday I had a guy tell me he could fix my a/c problem: compressor shutting of after a few minutes. He said it would need the expansion valve flush. I have the '87 300TDT and freon level or belt slipping are not the usual suspects.
|
#2
|
|||
|
|||
Does the a/c operate normally for 5-10 minutes, then the compressor disengage and not come back on for an extended period?
|
#3
|
|||
|
|||
Correct.
|
#4
|
|||
|
|||
Then I would suspect the evaporator temp regulator. It is supposed to disengage the compressor to prevent evaporator freeze-up, but it can fail so that it "trips" at a too-high temp. You could unplug it and jumper the plug and see if that solves your problem.
|
#5
|
||||
|
||||
Could also be a temperamental Klima relay or low pressure switch.
Sixto 87 300D |
#6
|
|||
|
|||
No easy way out, as always....
|
#7
|
|||
|
|||
Today I broke down and bought a new KLIMA relay- you were right on with the guess regarding a "temperamental" relay! Just a side observation: after I had a new unit in and a/c blowing cold air, I decided to take a look at the old one. It looked like it may have a darker spot on the board: how could it have happen with just 12v passing through?
|
#8
|
||||
|
||||
Don't DO This !
12Volts D.C. ain't anything like A.C...12 volts D.C. will stop your heart!
12 volts D.C. is enough power to weld a wrench dropped so that it contacts both poles... 12 volts D.C. will turn the tip of a glow plug so cherry red that you can brand cattle with it for about 5 minutes (AFTER it's disconnected). Think about it this way: Alternating Current switches Polarity back and forth. Direct Current is just straight power...