Wiring requirements for MIG welder
I just bought a Lincoln 175 HD MIG welder. My neighbor at my warehouse is a metal fabricator and he confirmed my suspicion that 220 was about the only way to go. My shop has 3 phase power coming into the box, which I don't really need, no circuits wired up at any rate, and only one 220 circuit, for the baseboard heater and it's a 20 amper. I need to put in a dedicated circuit going to the garage part of my shop, 50 feet away.
Lincoln says a 40 amp breaker is required. This would mean 8-2 with ground. I've seen a couple of web sites that claim 10-2 w/G and a 30 amp breaker is more than enough. My neighbor also thought 30 would do it. Whattyathink? |
Quote:
|
I have a Lincoln 175 TIG setup in my garage that is powered via a 30 amp circuit. According to the owners manual it requires a 70 amp 220 connection to deliver the full 175 amp rating. My setup works fine up until about the 100-110 amp level - then it will blow a circuit breaker. Since I use the machine mainly for fine work (sheet metal) I really don't care about about utilizing the higher end of the amp spectrum - I typically do most of my welding at the 20-40 amp level.
At the 100 amp level I can weld steel up to about a 1/4 inch plate and aluminum up to about 1/8 inch - If you are going to be dealing with materials thicker than this you are most likely going to need a higher amp service rating. |
Quote:
|
Run the largest capacity your main circuit panel will allow! It can be very useful for other things as well.
You can power your house with the garage 220 via a generator set-up. :eek: DO NOT ATTEMPT THIS UNLESS YOU KNOW WHAT YOU ARE DOING! When I did my garage I went with the largest my house panel would permit. |
my electrician buddy says NMB-10/2wg is only good for 25amps. PLus current drain from distances should be taken into consideration too.
|
Quote:
|
Quote:
On the 2 30 amp breakers, are you sure it's a good idea to have breakers that are rated higher then the wire? |
Good advice all around. I found an electric supply place that is getting me 50 ft. of 8-2 w/g for $1.26 a ft. which is a nickel less than Home Despot wanted for 10-2 (?!). I've run into this before -- HD seduces one into thinking that their prices are always lower and they're not.
I'm about 60 to 70% of an electrician -- I'm confident I can do this safely. I turn off the main breaker at the panel, of course, doubly important due to the 3 phase power in that box. The 3rd leg has a black cable feeding it with an orange band around it, the digital tester says it's 201 volts. Ouchy. |
Suggestion
Go over to "weldtalk.com" and you will get good and info u can count on there. A lot of certfied electricians there.
John |
Hey, good tip.
|
Quote:
As a licensed master electrician and electrical contractor, I'd recommend that you adhere strictly to the nameplate rating of the equipment and the NEC when implementing your installation. If you have any specific questions, ask here or PM me. |
Hey, that's quite an offer. I'm mostly a carpenter, and speaking of which, do you know the difference between a carpenter and an electrician?
The carpenter wasn't smart enough to be an electrician. That's not entirely true of course but if I had it to do over again, I'd have put in a decent apprenticeship as a plumber or electrician back when I was young enough to do it. I can do both to some degree but there are gaps in my knowledge. One thing I do know is that I stay away from that 3rd leg. I have nothing that utilizes that type of power. I understand it can run a seriously powerful motor and save you money on your electric bill while doing it. Maybe I'll find a need to use it someday and if I do, I believe I'll get a real electrician to do run the circuit. |
Quote:
|
Quote:
|
All times are GMT -4. The time now is 04:14 PM. |
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2024 Pelican Parts, LLC - Posts may be archived for display on the Peach Parts or Pelican Parts Website