home A/C, HVAC guys input needed here.

I have got a new place to live now its a 2100 sq ft two story with a living room that has tall celings.

The A/C unit is one item but the airhandler in the attic has two outlets which are going into two manifolds which air the lower and upper floors of the house.

The manifold air ducts have got electric dampers in them (which are a bit impossible to reach at this point of time due to me being a bit wary in fiddling with the attic. The dampers are controlled by a unit stuck to the handler furnace and is branded as trolAtemp

anyway - the 1st floor air registers blow really hard, almost if all air flow is coming out there, the upper floor has really poor air velocity out the registers - almost impossible to feel even at 2 inches from the registers.

Is this setting normal for cooling - or should it be the other way round.

Hot air goes up - hence upper floor is not as cool as the lower floor where there is a lot of cold air and a lot of air velocity at the registers.

there is a thermostat in the first floor too but it does not make much sense to me - its an old mercury bulb type - it does switch on the A/C if I manipulate it - but it was very dusty and set to 90 - so I left it there too.

__________________
2012 BMW X5 (Beef + Granite suspension model)

1995 E300D - The original humming machine (consumed by Flood 2017)
2000 E320 - The evolution (consumed by flood 2017)
Reply With Quote
  #2  
Old 07-21-2014, 05:13 PM
Registered User
 
Join Date: Mar 2014
Location: Coldest North America
Posts: 833
From the description it appears that the upper air supply damper is closed and the lower air supply damper is open. The dampers may not be operating correctly and the assistance of an HVAC controls tech will be required to sort it out.

Generally it's best to have most of the supply air delivered to the upper level where it's hottest as cool air will naturally sink to lower levels.

Where are the grilles for the air going back [return air] to the A/C unit air located?

Blow the dust out of the thermostst for it to operate correctly.
__________________
“Never attempt to teach a pig to sing; it wastes your time and annoys the pig.” ― Robert A. Heinlein
Reply With Quote
  #3  
Old 07-21-2014, 05:29 PM
Registered User
 
Join Date: Nov 2010
Location: TX
Posts: 3,978
Quote:
Originally Posted by John Galt View Post
From the description it appears that the upper air supply damper is closed and the lower air supply damper is open. The dampers may not be operating correctly and the assistance of an HVAC controls tech will be required to sort it out.

Generally it's best to have most of the supply air delivered to the upper level where it's hottest as cool air will naturally sink to lower levels.

Where are the grilles for the air going back [return air] to the A/C unit air located?

Blow the dust out of the thermostst for it to operate correctly.
Yes I also believe the upper air supply damper is closed and not responding.I have talked to a few guys but being summer - they have a selection of answers.

1 - system is too old - you would prolly need a full unit
2 - booked till end of september
3 - something else too.

thanks for the answer tho.

Im going to dig into the system and see if the damper is getting voltage or not

there are two return vents - one is on the upper floor and is 20x30 inches, the other is a 15x15 inch vent and is on the lower floor - the upper floor vent is placed such that it can be seen from anywhere in the lower living room.
__________________
2012 BMW X5 (Beef + Granite suspension model)

1995 E300D - The original humming machine (consumed by Flood 2017)
2000 E320 - The evolution (consumed by flood 2017)
Reply With Quote
  #4  
Old 07-21-2014, 05:42 PM
engatwork's Avatar
Registered User
 
Join Date: May 2000
Location: Soperton, Ga. USA
Posts: 13,667
Just going on feeling comfortable or not which floor do you prefer or are they both the same?

Would not surprise me if one of the thermostats controls predominately air distribution if system is working properly.
__________________
Jim
Reply With Quote
  #5  
Old 07-21-2014, 06:35 PM
davidmash's Avatar
Supercalifragilisticexpia
 
Join Date: Mar 2002
Location: Arlington, TX
Posts: 47,552
Quote:
Originally Posted by Zulfiqar View Post
Yes I also believe the upper air supply damper is closed and not responding.I have talked to a few guys but being summer - they have a selection of answers.

1 - system is too old - you would prolly need a full unit
2 - booked till end of september
3 - something else too.

thanks for the answer tho.

Im going to dig into the system and see if the damper is getting voltage or not

there are two return vents - one is on the upper floor and is 20x30 inches, the other is a 15x15 inch vent and is on the lower floor - the upper floor vent is placed such that it can be seen from anywhere in the lower living room.
Where in TX are you? I have a AC guy who charges $25 for a service call for diagnostic. Used him once and he seems pretty legit to me.
__________________
Sent from an agnostic abacus

2014 C250 21,XXX my new DD ** 2013 GLK 350 18,000 Wife's new DD**

- With out god, life is everything.
- God is an ever receding pocket of scientific ignorance that's getting smaller and smaller as time moves on..." Neil DeGrasse Tyson
- You can pray for me, I'll think for you.
- When you understand why you dismiss all the other possible gods, you will understand why I dismiss yours.
Reply With Quote
  #6  
Old 07-21-2014, 06:35 PM
davidmash's Avatar
Supercalifragilisticexpia
 
Join Date: Mar 2002
Location: Arlington, TX
Posts: 47,552
Quote:
Originally Posted by Zulfiqar View Post
Yes I also believe the upper air supply damper is closed and not responding.I have talked to a few guys but being summer - they have a selection of answers.

1 - system is too old - you would prolly need a full unit
2 - booked till end of september
3 - something else too.

thanks for the answer tho.

Im going to dig into the system and see if the damper is getting voltage or not

there are two return vents - one is on the upper floor and is 20x30 inches, the other is a 15x15 inch vent and is on the lower floor - the upper floor vent is placed such that it can be seen from anywhere in the lower living room.
Where in TX are you? I have a AC guy here in the DFW area who charges $25 for a service call for diagnostic. Used him once and he seems pretty legit to me.
__________________
Sent from an agnostic abacus

2014 C250 21,XXX my new DD ** 2013 GLK 350 18,000 Wife's new DD**

- With out god, life is everything.
- God is an ever receding pocket of scientific ignorance that's getting smaller and smaller as time moves on..." Neil DeGrasse Tyson
- You can pray for me, I'll think for you.
- When you understand why you dismiss all the other possible gods, you will understand why I dismiss yours.
Reply With Quote
  #7  
Old 07-21-2014, 08:11 PM
INSIDIOUS's Avatar
Not suffering fools today
 
Join Date: Jan 2014
Location: Tartarus Dorsa Mountains
Posts: 30,601
Does the upper return vent seem to be sucking air as strongly as the lower one? You can temporarily block either with a newspaper or something to see if the other is sucking.

The other obvious thing is to be sure the stat for upstairs is calling for cool so that it opens those dampers. Switched to 'cool' and turned down. Does cranking it either way have an effect?

Temp aid to equalize is block half the lower return forcing more of the conditioned air to pass the upper level.

Last edited by INSIDIOUS; 07-22-2014 at 12:12 AM.
Reply With Quote
  #8  
Old 07-21-2014, 08:28 PM
Registered User
 
Join Date: Mar 2014
Location: Coldest North America
Posts: 833
Quote:
Originally Posted by Zulfiqar View Post
Yes I also believe the upper air supply damper is closed and not responding....

thanks for the answer tho.

Im going to dig into the system and see if the damper is getting voltage or not

there are two return vents - one is on the upper floor and is 20x30 inches, the other is a 15x15 inch vent and is on the lower floor - the upper floor vent is placed such that it can be seen from anywhere in the lower living room.
That's a good start to finding out what is supposed to control the upper floor damper. Usually each zone has a separate thermostat to control that zone's damper, which opens the damper when the temperature is above the set point.

The biggest return vent is on the upper floor, so that's OK.
__________________
“Never attempt to teach a pig to sing; it wastes your time and annoys the pig.” ― Robert A. Heinlein
Reply With Quote
  #9  
Old 07-22-2014, 09:37 AM
Registered User
 
Join Date: Nov 2010
Location: TX
Posts: 3,978
Quote:
Originally Posted by davidmash View Post
Where in TX are you? I have a AC guy here in the DFW area who charges $25 for a service call for diagnostic. Used him once and he seems pretty legit to me.
Im in Houston
__________________
2012 BMW X5 (Beef + Granite suspension model)

1995 E300D - The original humming machine (consumed by Flood 2017)
2000 E320 - The evolution (consumed by flood 2017)
Reply With Quote
  #10  
Old 07-22-2014, 09:42 AM
Registered User
 
Join Date: Nov 2010
Location: TX
Posts: 3,978
Quote:
Originally Posted by John Galt View Post
That's a good start to finding out what is supposed to control the upper floor damper. Usually each zone has a separate thermostat to control that zone's damper, which opens the damper when the temperature is above the set point.

The biggest return vent is on the upper floor, so that's OK.
I am going to trace out the wiring for the upper stat, the lower one only has 3 wires in it, Either the thermostats are tied in parallel or the damper settings for lower and upper are reversed.

For the time being I have mounted three little black honeywell fans on the walls facing upwards which actually caused the upper floor to cool down real quick and the A/C then shut off. The fans look a bit cartoonish according to the Mrs.
__________________
2012 BMW X5 (Beef + Granite suspension model)

1995 E300D - The original humming machine (consumed by Flood 2017)
2000 E320 - The evolution (consumed by flood 2017)
Reply With Quote
  #11  
Old 07-22-2014, 09:45 AM
Registered User
 
Join Date: Nov 2010
Location: TX
Posts: 3,978
Quote:
Originally Posted by INSIDIOUS View Post
Does the upper return vent seem to be sucking air as strongly as the lower one? You can temporarily block either with a newspaper or something to see if the other is sucking.

The other obvious thing is to be sure the stat for upstairs is calling for cool so that it opens those dampers. Switched to 'cool' and turned down. Does cranking it either way have an effect?

Temp aid to equalize is block half the lower return forcing more of the conditioned air to pass the upper level.
There is no change at all in airflow with the stat set to heat either.
__________________
2012 BMW X5 (Beef + Granite suspension model)

1995 E300D - The original humming machine (consumed by Flood 2017)
2000 E320 - The evolution (consumed by flood 2017)
Reply With Quote
  #12  
Old 07-22-2014, 01:22 PM
davidmash's Avatar
Supercalifragilisticexpia
 
Join Date: Mar 2002
Location: Arlington, TX
Posts: 47,552
Quote:
Originally Posted by Zulfiqar View Post
Im in Houston
Never mind. Pretty sure he will not drive down there. lol
__________________
Sent from an agnostic abacus

2014 C250 21,XXX my new DD ** 2013 GLK 350 18,000 Wife's new DD**

- With out god, life is everything.
- God is an ever receding pocket of scientific ignorance that's getting smaller and smaller as time moves on..." Neil DeGrasse Tyson
- You can pray for me, I'll think for you.
- When you understand why you dismiss all the other possible gods, you will understand why I dismiss yours.
Reply With Quote
  #13  
Old 07-22-2014, 01:41 PM
MTI's Avatar
MTI MTI is offline
Registered User
 
Join Date: Nov 2002
Location: Scottsdale, Arizona
Posts: 10,626
Quote:
Originally Posted by Zulfiqar View Post
The fans look a bit cartoonish according to the Mrs.
Reply With Quote
  #14  
Old 07-22-2014, 03:39 PM
Banned
 
Join Date: May 2004
Location: Varies
Posts: 4,802
It's a box with a flapper valve in it. If you had to you could hook up a heater cable from the junkyard.
Reply With Quote
  #15  
Old 07-22-2014, 03:52 PM
Skid Row Joe's Avatar
Banned
 
Join Date: Oct 2007
Location: #KeepingAmericaGreat!
Posts: 7,071
If you bought the place - I'd look at my heating and cooling usage/bills to gauge whether I wanted to do an immediate R&R of the whole HVAC system. I don't think I could calculate how many times the new HVAC system I installed in my present home over a decade ago has saved me in power costs. Most any two-story will benefit cost wise over time from dual-systems, independent one another. -If you even use the second floor? Of course this all depends on your time horizon in this home too.

It also helped greatly Upping my home's attic R-value from 12 or 13 to R-45. As well doing an install of ridge-cap venting along the entire apex of the roof.

Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On




All times are GMT -4. The time now is 04:38 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2024 Pelican Parts, LLC - Posts may be archived for display on the Peach Parts or Pelican Parts Website -    DMCA Registered Agent Contact Page