Quote:
Originally Posted by gmercoleza
Overcharging can damage the compressor over time. It may not happen immediately, especially if there is a binary cutout switch installed. Those switches usually shut off the compressor at around 435 PSI, long before any seals would blow (unless there is an existing weakness, but that's another story). But higher pressures will definitely accelerate wear, as can generally be witnessed by the much shorter average lifespan of R12 to R134a converted systems; R134a pressures run in the neighborhood of 100psi more than R12 and really put stress on compressors which were originally designed for R12.

Pressures being out of spec can tell you if there is too much oil in the system, if the TXV is plugged, or if there is some other blockage in the system. It can help diagnose faulty switches and even tell you if the charge is simply low (the most favorable scenario). And yes, condensor blockage would also be detectable with gauges though there would likely be other indicators of that.
Thanks for your explanation. I don't have a problem at the moment, but have been immensely appreciative of the level of expertise and willingness to share information here.
__________________
" We have nothing to fear but the main stream media itself . . . ."- Adapted from Franklin D Roosevelt for the 21st century

OBK #55

1998 Lincoln Continental - Sold
Max 1984 300TD 285,000 miles - Sold
The Dee8gonator 1987 560SEC 196,000 miles - Sold
Orgasmatron - 2006 CLS500 90,000 miles
2002 C320 Wagon 122,000 miles
2016 AMG GTS 12,000 miles
Reply With Quote