Cool, what kind of facility do you manage, if you're allowed to say?

Mechanically engines definitely smoke a lot more on full load application than the common rail engines. Fortunately I haven't come across a mechanically injected engine in quite a while. Data centers always want the newest and best due to reliability reasons.

And you're correct about the engine being kept warm. Also the engines have a pre-lube pump that runs on intervals, to keep the oil film maintained on the bearing surfaces.

All this comes from the NFPA 101/NEC section 70x/JAHCO requirements that you are on the bus in less than 10 seconds. When you hit the start signal, it's pretty much clunk (starter solenoid), a second or 2 of crank, fire within the first revolution, full 1800/min about 3-4 seconds later, rpms stabilized, exciter enabled, and you are at 480 V and 60 Hz in about 6 seconds. That gives you enough time for your transfer equipment to get the generator on the bus and beat the 10 second clock.