Shoddy plumbing work...

I needed to have a water heater installed in my family's house on short notice. If I had a bit more time, I'd have done the work myself. Called a local plumber, guys who came out were as American as apple pie, so please no whining about immigrants and quality of work...

Turns out:
(1) They upgraded the vent pipe from 3" to 4". They said that 4" is no longer code, but the township inspector "likes to see it." Only problem was, when they sealed it to the chimney, they left huge gaps, which fortunately, I noticed.
(2) They used crimp/o-ring fittings on copper pipe, didn't sweat the pipes. Surely a metal-metal joint would last longer than a crimp with an o-ring that will deteriorate.
(3) They put the water heater directly on the cement floor, with no standoffs. They said they'd have to shorten the gas pipe to put the standoffs, but they did that anyway since the new heater had the gas nipple in a different location.
(4) Put an expansion tank, with no support. They grudgingly put in a copper strap that is barely even tight.

All this quality work for the princely sum of $1200.

EDIT: they didn't turn on the water to the house fully -- made taking a shower a bit difficult till we realized what was going on


Last edited by spdrun; 01-18-2017 at 06:41 PM.
Reply With Quote
  #2  
Old 01-18-2017, 08:17 PM
chilcutt's Avatar
Anywhere I Roam
 
Join Date: Mar 2008
Location: Singapore
Posts: 13,161
Typical 'Slam Bam Thank You Mam'.
Did they install dielectric unions ?
__________________
CHILCUTT~
The secret to a long life. Is knowing when it is time to leave.
Reply With Quote
  #3  
Old 01-18-2017, 08:25 PM
Dubyagee's Avatar
All fields are required
 
Join Date: Jul 2006
Location: SE
Posts: 8,722
Some heaters come with them already.
Reply With Quote
  #4  
Old 01-18-2017, 10:31 PM
Registered User
 
Join Date: May 2011
Location: NYC
Posts: 6,030
Quote:
Originally Posted by Dubyagee View Post
Some heaters come with them already.
Looks like it did.
Reply With Quote
  #5  
Old 01-18-2017, 11:14 PM
t walgamuth's Avatar
dieselarchitect
 
Join Date: Apr 2005
Location: Lafayette Indiana
Posts: 38,632
Nothing you describe sounds necessarily shoddy to me. Its how they do it now. If you want it done as it would have been done in the eighties or seventies you can get it done but it will cost a lot more.
__________________
[SIGPIC] Diesel loving autocrossing grandpa Architect. 08 Dodge 3/4 ton with Cummins & six speed; I have had about 35 benzes. I have a 39 Studebaker Coupe Express pickup in which I have had installed a 617 turbo and a five speed manual.[SIGPIC]

..I also have a 427 Cobra replica with an aluminum chassis.
Reply With Quote
  #6  
Old 01-18-2017, 11:34 PM
chilcutt's Avatar
Anywhere I Roam
 
Join Date: Mar 2008
Location: Singapore
Posts: 13,161
Quote:
Originally Posted by spdrun View Post
Looks like it did.
Good. Nothing you can do now except make sure you drain it properly once or twice a year to release any sediment..
As long as your folks have hot water, who cares how it gets delivered.
__________________
CHILCUTT~
The secret to a long life. Is knowing when it is time to leave.
Reply With Quote
  #7  
Old 01-19-2017, 12:01 AM
Registered User
 
Join Date: May 2011
Location: NYC
Posts: 6,030
Quote:
Originally Posted by t walgamuth View Post
Nothing you describe sounds necessarily shoddy to me. Its how they do it now. If you want it done as it would have been done in the eighties or seventies you can get it done but it will cost a lot more.
Sweating the joints would have taken maybe a minute more per joint -- a metal-metal bond is more reliable than rubber-to-copper. Leaving gaps in the cement around the vent pipe is just bad work and a CO hazard. Same with not supporting the expansion tank -- it's bad work, a leak hazard since it stresses the pipe joints, and takes a few minutes to do right.

The install would have flunked inspection as it was, and rightly so. Unfortunately, you have to wait a few weeks for an inspection appointment in that town.

Oh, and the kicker? They didn't re-open the water valve to the house fully. When I took a shower after I finished cleaning after them, there was next to no water pressure, and the pipes were making a screaming sound.
Reply With Quote
  #8  
Old 01-19-2017, 03:50 AM
cmac2012's Avatar
Renaissances Dude
 
Join Date: Dec 2004
Location: Redwood City, CA
Posts: 34,120
Does that price include the heater or was that for labor only?
__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
  #9  
Old 01-19-2017, 07:26 AM
t walgamuth's Avatar
dieselarchitect
 
Join Date: Apr 2005
Location: Lafayette Indiana
Posts: 38,632
I'll have to agree on the cement gaps and the support for the tank...
__________________
[SIGPIC] Diesel loving autocrossing grandpa Architect. 08 Dodge 3/4 ton with Cummins & six speed; I have had about 35 benzes. I have a 39 Studebaker Coupe Express pickup in which I have had installed a 617 turbo and a five speed manual.[SIGPIC]

..I also have a 427 Cobra replica with an aluminum chassis.
Reply With Quote
  #10  
Old 01-19-2017, 12:57 PM
Registered User
 
Join Date: Oct 2012
Posts: 5,924
At 1200.00 it should include the heater. Yet you never know today. The younger generation seem to be happy with the non sweated copper pipe connections.

I was sitting here wondering if a good plumber would have used them in your situation. Or is it a case since ninety percent or more on domestic applications all plastic is now used.

Has it perhaps increased their comfort level with various forms of compression devices? My son in law seems to have a real comfort zone with them and used them a lot in repair situations on old copper systems. Come to think about it when he was between real jobs and was maintaining two large motels about thirty years old his questions for me where endless at the time.

Last edited by barry12345; 01-19-2017 at 01:07 PM.
Reply With Quote
  #11  
Old 01-19-2017, 02:43 PM
t walgamuth's Avatar
dieselarchitect
 
Join Date: Apr 2005
Location: Lafayette Indiana
Posts: 38,632
I just a week ago had to replace about 50' of beautiful copper drain lines which rotted away from the inside. They looked great until they came apart and dropped gallons of nasty poo water on the basement floor of my building. I shudder to guess what the bill will be for that work.

They put in new pvc.
__________________
[SIGPIC] Diesel loving autocrossing grandpa Architect. 08 Dodge 3/4 ton with Cummins & six speed; I have had about 35 benzes. I have a 39 Studebaker Coupe Express pickup in which I have had installed a 617 turbo and a five speed manual.[SIGPIC]

..I also have a 427 Cobra replica with an aluminum chassis.
Reply With Quote
  #12  
Old 01-19-2017, 03:19 PM
Registered User
 
Join Date: Jan 2002
Posts: 18,350
Are you referring to shark fittings? I like them and use them myself. I've wondered about the life span of the o-rings but I haven't had any fail yet and some are about 6 years old. I've had soldered joints fail in the past so they're not guaranteed. I also use Pex now instead of copper. Where I attach Pex to copper I use a shark fitting.
I put in a water heater a few weeks ago. $540 for a 50 gallon gas heater from Home Depot and a couple of hours work. Didn't use shark fittings or pex because the old heater had flexible copper connectors. Worst part was getting the old heater up the stairs from the basement, god, those things get heavy after being in use for 10 yrs.
__________________
1977 300d 70k--sold 08
1985 300TD 185k+
1984 307d 126k--sold 8/03
1985 409d 65k--sold 06
1984 300SD 315k--daughter's car
1979 300SD 122k--sold 2/11
1999 Fuso FG Expedition Camper
1993 GMC Sierra 6.5 TD 4x4
1982 Bluebird Wanderlodge CAT 3208--Sold 2/13
Reply With Quote
  #13  
Old 01-19-2017, 04:42 PM
t walgamuth's Avatar
dieselarchitect
 
Join Date: Apr 2005
Location: Lafayette Indiana
Posts: 38,632
Most people just throw them aside and leave them for the next owners.
__________________
[SIGPIC] Diesel loving autocrossing grandpa Architect. 08 Dodge 3/4 ton with Cummins & six speed; I have had about 35 benzes. I have a 39 Studebaker Coupe Express pickup in which I have had installed a 617 turbo and a five speed manual.[SIGPIC]

..I also have a 427 Cobra replica with an aluminum chassis.
Reply With Quote
  #14  
Old 01-19-2017, 05:01 PM
Dubyagee's Avatar
All fields are required
 
Join Date: Jul 2006
Location: SE
Posts: 8,722
Mine is in the attic. I think it was put up there before the house was finished. I missed that day during the build 13 years ago. Going to be a rough one to swap.
Reply With Quote
  #15  
Old 01-19-2017, 06:25 PM
Registered User
 
Join Date: Jan 2002
Posts: 18,350
Go tankless.

__________________
1977 300d 70k--sold 08
1985 300TD 185k+
1984 307d 126k--sold 8/03
1985 409d 65k--sold 06
1984 300SD 315k--daughter's car
1979 300SD 122k--sold 2/11
1999 Fuso FG Expedition Camper
1993 GMC Sierra 6.5 TD 4x4
1982 Bluebird Wanderlodge CAT 3208--Sold 2/13
Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On




All times are GMT -4. The time now is 09:10 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2024 Pelican Parts, LLC - Posts may be archived for display on the Peach Parts or Pelican Parts Website -    DMCA Registered Agent Contact Page