2 110 legs and a neutral Bus,8-3 with ground w/1 30 Murray breaker on each {2} hot legs.Better safe than sorry.
This welder doesn't need a neutral wire, and the box that fits their 220 cord jack, a Nema 6-50, only has terminals for the 2 110 wires and a ground.

On the 2 30 amp breakers, are you sure it's a good idea to have breakers that are rated higher then the wire?