It is most likely low refrigerant level, but a restriction in the system can cause the same thing, which is insufficient refrigerant flow at the TXV.
The best way to tell which is the case is to evacuate the system and recharge by weight. If the pressures are then within specs, you're good to go. If not, you're not.
|