|
You shouldn't go over 80% of the listed breaker capacity. For a 60 amp breaker you don't want to draw more than 48 amps.
If it says 30 on the outside panel then you should be OK. You read the FLA rating right?
Also make sure the total draw on the breaker doesn't include the inside fan unit. If it does then you have to add the fan rating to the total amp draw.
Always use FLA (Full Load Amp) rating.
Danny
__________________
1984 300SD Turbo Diesel 150,000 miles
OBK member #23
(\__/)
(='.'=) This is Bunny. Copy and paste bunny into your
(")_(") signature to help him gain world domination
|