Originally Posted by vstech View Post
if you pressure tested free of leaks, vacuumed it out, and charged with the correct weight of R12, the coils are clean and new, the aux fan is running... it's doing all it can do.
the SDL has which compressor? sanden?

bubbles mean the liquid column of refrigerant is not solid. it's either low on refrigerant, or the ambient temp is above the design... (110°F certainly qualifies) what's the high pressure? what's the condenser liquid temp? I would do everything in my power to VERIFY zero outside air is mixing in.
aux fan is running well. Correct amount of R12 I am nor so sure. i think I charged more but I am always a bit uncertain with the old cans...they sometimes seem to be low on R12.
I believe high side is around 250psi at 100F-110F ambient. Outside air is not mixing here.
I can see bubbles at these ambient temperatures...it is never below these temps right now and I see bubble all the time.
No idea about the condenser liquid temps. I can measure. Where? At the out let to the drier? I have a infrared thermometer.