Question Converting heating boiler from oil to gas. Any experience?

Back in 2000 we replaced our fullsize van-sized, asbestos-laden boiler with a Smith Cast Iron Boiler 28A which is closer in size to a large refridgerator laying on it's side (and more BTU's). It currently has an oil burner and we burn about 60 gals. of HHO a day in the winter supplying steam for heat.

Our fuel oil tanks are due for replacement (or removal) within the next couple of years. Our options are somewhat limited since we're in a historic district. Above ground on a containment pad would be the preferred choice but it would never fly so it would have to be another inground tank.

We got to thinking, since we have gas service already for the hot water heater, is it possible to replace the oil burner on the boiler with a gas burner? I can't think of any reason it couldn't. Doing so has a lot of advantages for us. 1) Takes the tank out of the equation all together, just have to pay to get the old one removed. 2) Easier to budget out the heating fuel expenses since it would be metered over a given period of time vs. whenever the oil company got around to delivering it (often to empty the no so clean stuff out of their own storage tank before refilling), sometimes twice a week. 3) Eliminates the possibilty of running out of fuel (which has happened during especially cold stretches. 4)The gas company offers full energy audits for their customers which might point us towards some significant energy savings across the board.

With the price of HHO and natural gas fluctuating all over the place, it's probably a wash over the long run. Even if it does cost more, the savings from not replacing the tank gives us a head start. The fuel cost is secondary anyway, we don't mind paying a bit more for a cleaner burning fuel that eliminates some of the headaches of HHO. And I won't even go into the politics of NG and HHO.

Anybody do it commercially or residentially? My brother placed a call to CNG to have a rep. come out but hasn't gotten an appointment yet.

__________________

1980 300TD-China Blue/Blue MBTex-2nd Owner, 107K (Alt Blau) OBK #15
'06 Chevy Tahoe Z71 (for the wife & 4 kids, current mule) '03 Honda Odyssey (son #1's ride, reluctantly) '99 GMC Suburban (255K+ miles, semi-retired mule) 21' SeaRay Seville (summer escape pod)
Reply With Quote
  #2  
Old 10-03-2008, 09:14 AM
Mister Byrnzoil's Avatar
Currently Benzless :(
 
Join Date: Dec 2004
Location: Palm Springs, CA
Posts: 777
Quote:
Originally Posted by SwampYankee View Post
It currently has an oil burner and we burn about 60 gals. of HHO a day in the winter supplying steam for heat.
you burn $200 a day for 4-5 months?
__________________
Cheers,
Robert
Reply With Quote
  #3  
Old 10-03-2008, 09:43 AM
Registered User
 
Join Date: Jan 2006
Location: Tucson, AZ
Posts: 5,338
Check with the boiler manufacturer or company which installed the unit. My experience with any of the conversions has been a dismal experience at best. They tend to use different technologies considering the different heating properties of the fuels (oil heat is considered a "slow" expanding type of flame to heat a broad surface whereas NG is used to "spot heat" an area and conduction is used to spread the heat) and usually the firebox has to be remade.

This is old experience (40 years ago) so depending on the age of your boiler it may not be applicable.

I'd go for the conversion because you can easily convert it to propane with a simple orifice change down the road.
Reply With Quote
  #4  
Old 10-03-2008, 09:52 AM
Registered User
 
Join Date: Apr 2005
Location: Rockville MD
Posts: 833
I take it this is for a large building. Has anyone done a heat loss calculation on the building to make sure your boiler is sized properly?

There are gas burners that basically replace the oil unit. They are called power gas burners, and operate on the same air tube principle. As long as your Smith boiler is certified to run with gas, it shouldn't be a problem at all. But if the boiler is oversized it becomes inefficient.
__________________
1985 380SE Blue/Blue - 230,000 miles
2012 Subaru Forester 5-speed
2005 Toyota Sienna
2004 Chrysler Sebring convertible
1999 Toyota Tacoma
Reply With Quote
  #5  
Old 10-03-2008, 10:12 AM
SwampYankee's Avatar
New England Hick
 
Join Date: Sep 2006
Location: CT
Posts: 1,501
Quote:
Originally Posted by Mister Byrnzoil View Post
you burn $200 a day for 4-5 months?
Yep, depending on the cost of fuel. I think our total bill last year was $34K, which includes the tapering in and out on either side of the winter months.
__________________

1980 300TD-China Blue/Blue MBTex-2nd Owner, 107K (Alt Blau) OBK #15
'06 Chevy Tahoe Z71 (for the wife & 4 kids, current mule) '03 Honda Odyssey (son #1's ride, reluctantly) '99 GMC Suburban (255K+ miles, semi-retired mule) 21' SeaRay Seville (summer escape pod)

Last edited by SwampYankee; 10-03-2008 at 10:28 AM.
Reply With Quote
  #6  
Old 10-03-2008, 10:15 AM
SwampYankee's Avatar
New England Hick
 
Join Date: Sep 2006
Location: CT
Posts: 1,501
Quote:
Originally Posted by Mike D View Post
Check with the boiler manufacturer or company which installed the unit. My experience with any of the conversions has been a dismal experience at best. They tend to use different technologies considering the different heating properties of the fuels (oil heat is considered a "slow" expanding type of flame to heat a broad surface whereas NG is used to "spot heat" an area and conduction is used to spread the heat) and usually the firebox has to be remade.

This is old experience (40 years ago) so depending on the age of your boiler it may not be applicable.

I'd go for the conversion because you can easily convert it to propane with a simple orifice change down the road.
Thanks Mike. At some point a CNG rep should be stopping by to let us know what's doable and what's not. I'd like to think a "newer" boiler would be capatible, or at least convertible, with multiple fuel burners but I don't know.
__________________

1980 300TD-China Blue/Blue MBTex-2nd Owner, 107K (Alt Blau) OBK #15
'06 Chevy Tahoe Z71 (for the wife & 4 kids, current mule) '03 Honda Odyssey (son #1's ride, reluctantly) '99 GMC Suburban (255K+ miles, semi-retired mule) 21' SeaRay Seville (summer escape pod)
Reply With Quote
  #7  
Old 10-03-2008, 10:25 AM
SwampYankee's Avatar
New England Hick
 
Join Date: Sep 2006
Location: CT
Posts: 1,501
Quote:
Originally Posted by raymr View Post
I take it this is for a large building. Has anyone done a heat loss calculation on the building to make sure your boiler is sized properly?

There are gas burners that basically replace the oil unit. They are called power gas burners, and operate on the same air tube principle. As long as your Smith boiler is certified to run with gas, it shouldn't be a problem at all. But if the boiler is oversized it becomes inefficient.
Roughly 40K sq.ft. of fairly inefficient (old woodframe single pane windows, wood overhead doors on the loading dock, no interior roof insulation-does have a layer of foam over the corrugated metal and under the rubber roof) warehouse. When we replaced the old boiler they did take everything into consideration (as far as we know) to determine the proper size.

I did manage to find the Smith website and they list the 28A as being Light Oil, Gas and Light Oil/Gas (uses one as backup?)capable. Would that make it a safe assumption that it might be as simple as a burner swap?

We're planning on addressing the inefficiencies we already know of (windows, doors and insulation) as well as the ones they discover during the energy audit. The windows on the south side of the building were replaced about 10 years ago with double pane vinyl, but that side isn't visible from the street. Street-side we might need to go with a storm window of some sort depending on what options the HD determines appropriate.
__________________

1980 300TD-China Blue/Blue MBTex-2nd Owner, 107K (Alt Blau) OBK #15
'06 Chevy Tahoe Z71 (for the wife & 4 kids, current mule) '03 Honda Odyssey (son #1's ride, reluctantly) '99 GMC Suburban (255K+ miles, semi-retired mule) 21' SeaRay Seville (summer escape pod)
Reply With Quote
  #8  
Old 10-03-2008, 11:03 AM
Registered User
 
Join Date: Apr 2005
Location: Rockville MD
Posts: 833
Quote:
Originally Posted by SwampYankee View Post
Roughly 40K sq.ft. of fairly inefficient (old woodframe single pane windows, wood overhead doors on the loading dock, no interior roof insulation-does have a layer of foam over the corrugated metal and under the rubber roof) warehouse. When we replaced the old boiler they did take everything into consideration (as far as we know) to determine the proper size.

I did manage to find the Smith website and they list the 28A as being Light Oil, Gas and Light Oil/Gas (uses one as backup?)capable. Would that make it a safe assumption that it might be as simple as a burner swap?
On residential systems, it is as simple as a burner swap, provided it is hooked up by a qualified technician. In fact some people keep both burners in case one fuel has a supply/price problem - then they just swap in the burner of choice. But then you would need to keep those oil tanks around.

Are you drawing outside air for burner combustion?
__________________
1985 380SE Blue/Blue - 230,000 miles
2012 Subaru Forester 5-speed
2005 Toyota Sienna
2004 Chrysler Sebring convertible
1999 Toyota Tacoma
Reply With Quote
  #9  
Old 10-03-2008, 11:30 AM
SwampYankee's Avatar
New England Hick
 
Join Date: Sep 2006
Location: CT
Posts: 1,501
Quote:
Originally Posted by raymr View Post
On residential systems, it is as simple as a burner swap, provided it is hooked up by a qualified technician. In fact some people keep both burners in case one fuel has a supply/price problem - then they just swap in the burner of choice. But then you would need to keep those oil tanks around.

Are you drawing outside air for burner combustion?
The price of each source is so up and down we'd probably just bite the bullet and go strictly gas so that we could remove the environmental liability issue of the tanks all together. We certainly wouldn't be tackling it ourselves, it'd be left to a tech.

And yes.
__________________

1980 300TD-China Blue/Blue MBTex-2nd Owner, 107K (Alt Blau) OBK #15
'06 Chevy Tahoe Z71 (for the wife & 4 kids, current mule) '03 Honda Odyssey (son #1's ride, reluctantly) '99 GMC Suburban (255K+ miles, semi-retired mule) 21' SeaRay Seville (summer escape pod)
Reply With Quote
  #10  
Old 10-03-2008, 11:58 AM
pawoSD's Avatar
Dieselsüchtiger
 
Join Date: Oct 2004
Location: Grand Rapids, MI
Posts: 15,438
With costs that high to heat the place wouldn't it make sense to do some efficiency upgrades (windows....doors....more insulation) to the building??) !!

Now we all know why diesel is so expensive! Its all flowing into your tanks!
__________________
-diesel is not just a fuel, its a way of life-
'15 GLK250 Bluetec 118k - mine - (OC-123,800)
'17 Metris(VITO!) - 37k - wifes (OC-41k)
'09 Sprinter 3500 Winnebago View - 62k (OC - 67k)
'13 ML350 Bluetec - 95k - dad's (OC-98k)
'01 SL500 - 103k(km) - dad's (OC-110,000km)
'16 E400 4matic Sedan - 148k - Brothers (OC-155k)
Reply With Quote
  #11  
Old 10-03-2008, 12:12 PM
dynalow's Avatar
Registered User
 
Join Date: Feb 2002
Posts: 1,599
Quote:
Originally Posted by SwampYankee View Post
The price of each source is so up and down we'd probably just bite the bullet and go strictly gas so that we could remove the environmental liability issue of the tanks all together. We certainly wouldn't be tackling it ourselves, it'd be left to a tech.

And yes.
My advice is to get the tank out of the ground pronto. Found this (old) article which may interest you in CT.
Is this your home or business we're talking about?
$200 a day to heat a house? Must be Windsor Castle, huh?

Removal of Underground Storage Tanks
By Daniel E. Kleinman of Levy & Droney P.C.

The scenario is becoming commonplace...

Sellers list their residence for sale. Buyers submit an offer conditioned upon the removal of a 25-year-old underground storage tank (UST) which is to be replaced with one or more new indoor tanks. Sellers have never had any problems with their UST. It will cost approximately $2,500.00 to remove and replace the UST. What is Seller's statutory, as opposed to contractual, obligation regarding the removal of the UST?

Three bodies of law regulate USTs: Federal, State and Municipal. The Resource Conservation and Recovery Act of 1976, as amended in particular by the Hazardous and Solid Waste Amendments of 1984 (HSWA), establishes a federal regulatory program for USTs. Under the Act, an "underground storage tank" is defined as "any one or combination of tanks (including underground pipes connected thereto) which is used to contain an accumulation of regulated substances, and the volume of which [is]ten percent (10%) or more beneath the surface of the ground" Heating oil is defined as a "regulated substance" under the Act. However, USTs which are used to store heating oil to be consumed on the premises where stored are not included under the definition of a UST. Therefore, the typical residential closing involving a UST would fall outside the scope of Federal regulations.

While Connecticut environmental regulations deal with USTs, they only apply to a "facility which serves any commercial, industrial, institutional, public or other building, including but not limited to hotels and motels, boarding houses, hospitals, nursing homes and correctional institutions, but not including residential buildings." (See Section 22A-449(d)-1(a)(2)). However, Connecticut Regulations do apply to a UST in excess of 2,100 gallons where the structure is not used solely as a dwelling. Again, the typical residential closing involving a UST would fall outside the scope of the State regulations. Finally, some municipalities in Connecticut have stepped into the void and created their own ordinances dealing with USTs. The Town of Simsbury, for example, has enacted regulations (Chapter 139, Simsbury Code) controlling the modification, installation, maintenance and removal of USTs in connection with residential buildings of three units or less.

According to Simsbury Selectman Joel Mandell, a Levy & Droney Real Estate Partner, "The regulations have worked well. We've caused a lot of old, potentially problem tanks to be removed." Other towns are studying the need for similar regulations. However, according to Mark D. Vasington of the Connecticut Attorney Title Insurance Company, "such detailed local regulations are to date more the exception than the rule." He indicates that data compiled by the Connecticut Department of Environmental Protection shows that less than twenty-five percent (25%) of the local governments in the State have enacted specific ordinances governing the use and removal of USTs.

Even if no ordinance or regulation exists for the mandatory removal of a UST in your community, Sellers should be aware of specific permitting requirements which may exist in connection with the voluntary removal of their UST. For instance, the local fire marshal must be notified and be present when the tank is removed to check for possible contamination. If contamination is found, the owner will be required to remove and clean up the contamination. Homeowners should use a licensed contracting company to remove the UST. The company should provide a detailed fee quote in writing as to the nature and extent of the services to be rendered including any additional costs of potential cleanup. The company should also provide a written report regarding removal of the tank, whether any contamination was present, and disposition of the tank and contaminated soil.

At a minimum, Sellers should also be sure to make full disclosure of the existence of a UST as required by the Department of Consumer Protection in the Residential Property Condition Disclosure Report delivered to prospective Buyers. Should you have any questions, members of our real estate practice group will be happy to advise and assist you.

As a society, we have become much more environmentally sensitive over the years. It is likely, therefore, that the trend at all levels of government will be toward greater regulation of residential USTs in the future.

In summary, remember these important points:

Federal and state laws do not govern typical residential USTs no matter how large.


Local ordinances may apply. Check the Town code in which the property is located for references to USTs.


As stricter laws are enacted, the costs of removal will increase. It may be less expensive to consider voluntary removal of the UST now as it may turn out to be more costly in the future.


Replacement of an old UST with a new in-ground tank may not be in your long-term interests if laws governing USTs become more restrictive.


As a Seller, protect yourself in the Sales Agreement against excessive removal and cleanup costs by allowing Seller to terminate the contract if those costs exceed a predetermined amount.

© 1998
Levy & Droney P.C.
Reply With Quote
  #12  
Old 10-03-2008, 12:57 PM
SwampYankee's Avatar
New England Hick
 
Join Date: Sep 2006
Location: CT
Posts: 1,501
Quote:
Originally Posted by pawoSD View Post
With costs that high to heat the place wouldn't it make sense to do some efficiency upgrades (windows....doors....more insulation) to the building??) !!

Now we all know why diesel is so expensive! Its all flowing into your tanks!
We will address all of that, some already has been at least in part. For the previous generations energy use was an afterthought. My brother and I look at it as an investment, something that will add to the bottom line in the coming years. My father does see the value in it, it's just not his #1 or #2 priority. As a privately held corp. we try to end up with as little net profit as possible (while still pleasing the bank, a good chunk goes towards employee bonuses and dividends to the stockholders). Lets just say that fuel oil and electrical costs often dwarf our bottom line at the end of the FY. Any savings goes right towards that and I bet it wouldn't take too much (relatively speaking) to get to a 10-15% reduction.

It boggles my mind to think what some of these factories must use energy-wise, we're just 40K sq.ft. of storage and light manufacturing. And it's not like the winds are whipping through the building in the winter either.
__________________

1980 300TD-China Blue/Blue MBTex-2nd Owner, 107K (Alt Blau) OBK #15
'06 Chevy Tahoe Z71 (for the wife & 4 kids, current mule) '03 Honda Odyssey (son #1's ride, reluctantly) '99 GMC Suburban (255K+ miles, semi-retired mule) 21' SeaRay Seville (summer escape pod)
Reply With Quote
  #13  
Old 10-03-2008, 01:04 PM
SwampYankee's Avatar
New England Hick
 
Join Date: Sep 2006
Location: CT
Posts: 1,501
Quote:
Originally Posted by dynalow View Post
My advice is to get the tank out of the ground pronto. Found this (old) article which may interest you in CT.
Is this your home or business we're talking about?
$200 a day to heat a house? Must be Windsor Castle, huh?
No, it's our building. The tank currently in the ground was put there just over 20 years ago, there were no issues then so I don't foresee and issues there now.

Mr. Levy is a customer of ours. He is part-owner of the New Britain Rock Cats, the Twins AA affiliate.
__________________

1980 300TD-China Blue/Blue MBTex-2nd Owner, 107K (Alt Blau) OBK #15
'06 Chevy Tahoe Z71 (for the wife & 4 kids, current mule) '03 Honda Odyssey (son #1's ride, reluctantly) '99 GMC Suburban (255K+ miles, semi-retired mule) 21' SeaRay Seville (summer escape pod)
Reply With Quote
  #14  
Old 10-03-2008, 01:21 PM
dynalow's Avatar
Registered User
 
Join Date: Feb 2002
Posts: 1,599
Quote:
Originally Posted by SwampYankee View Post
No, it's our building. The tank currently in the ground was put there just over 20 years ago, there were no issues then so I don't foresee and issues there now.

Mr. Levy is a customer of ours. He is part-owner of the New Britain Rock Cats, the Twins AA affiliate.
He's probably a good guy to talk to about the law and liability on UST removal (or defend you).
Here in NJ, home, underground tanks are a real PITA for owners. Commercial or residential. My family sold some property to a Government body and had to remove the hho tank, with a Health Dept. rep on site. This tank never leaked, but after 30 years enough spillage had seeped into the ground, we really had to dig a big hole to remove all the bad dirt. And the Removal guy told me that one or two more scoops of the front end loader would have reached the water table. Then I would have had real problems. Monitoring wells, etc, etc, As it was, I obtained an NFA letter from DEP "No further action" I guard it like gold. Liability runs with all previous ownership in this state, so I look on it as a get out of jail free card.

Are there any state or gas company credit ($$) incentive programs to convert to NG? Even if you had to get a new boiler, the payback period would probably be short.

Good luck man, and close the door!
Reply With Quote
  #15  
Old 10-03-2008, 02:12 PM
Hatterasguy's Avatar
Zero
 
Join Date: Nov 2002
Location: Milford, CT
Posts: 19,318
Under ground tanks are tough, more so if they are leaking. Sometimes your better off just pumping it dry and leaving it. Of course there are other options which I ain't putting on a public forum.

Anyway the old house I am buying this Wednesday has a 50 year old oil boiler. But they were smart enough to run a good sized gas line into the house for the stove, and branched it off if you ever wanted to convert. So we got a price $2,500 I think to install a new gas furnance. Hopefully thats a good selling feature.

The downside is I have 200 gallons of home heating oil that needs to go somewhere...I wonder where.

__________________
2016 Corvette Stingray 2LT
1969 280SE
2023 Ram 1500
2007 Tiara 3200
Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On