HVAC question...

Guys, I have a fairly new system for the upstairs - heat pump, R410/puron, scroll compressor. When it was installed, it was supposed to a fairly high end unit.

Well now, about 6 years later, it won't start. When the compressor tries to run, it just buzzes for about 5 seconds then clicks and quits. Then, about 10 seconds later, it does it again and keeps repeating but never gets started.

I can probably figure it out eventually, either the starter capacitor or contactor but if anyone knows for sure, it would sure save me a lot of time.

Thanks for any help you can give!

__________________
-Evan


Benz Fleet:
1968 UNIMOG 404.114
1998 E300
2008 E63


Non-Benz Fleet:
1992 Aerostar
1993 MR2
2000 F250

Last edited by KarTek; 01-30-2011 at 07:13 PM.
Reply With Quote
  #2  
Old 01-26-2011, 05:49 PM
mgburg's Avatar
"Illegal" 3rd Dist. Rep.
 
Join Date: May 2006
Location: Onalaska, WI.
Posts: 221
I've seen this problem with some AC units.

There are a few pressure switches ... usually one on each side of the compressor.

One's a High and the other's a Low Pressure switch.

With the system off, the pressure on both sides of the compressor will "even out" - since it's a closed-loop system, the pressure will equalize the longer the system is idle or not pumping.

But, when the pump starts, there's usually a "delay" switch that will prevent the compressor from shutting off for a preset time until the system has a chance to build up the right pressures on both sides of the compressor...lower pressure on the supply-side to the compressor and high-pressure on the exit side of the compressor.

If the "delay shut-off" relay drops out and either one of the the pressure switches is in an "off" state or "THERE'S SOMETHING WRONG HERE!" state, then the compressor shuts off for a predetermined time, then it will either try again or in a more expensive situation, trip out and then send an alarm to a monitoring point or station.

Since it's been 6 years since you've had it installed, the question, first, would be: When was the last, if ever, time you had the unit serviced? If never, now's the time to call in the calvary.

The best time for doing any of this work is usually during the begining of the cooling season for ACs...the service techs like to see the ambient air temperature around 75° to 80° and a relative humidity level of something just about the top end of "comfortable" - whatever that is...

As for a HP? That's their call. They probably have a "balance point" for ambient air and humidity that's an all-around good testing/setting-up point that works both sides of the seasonal setup for their gear.

GL and let us know what happens!

BTW: I've seen AC Techs use a standard tire guage just to check to see if the system has ANY gas in it. CAUTION; NEVER WHILE THE SYSTEM WAS ON/RUNNING. ONLY WHEN IT WAS OFF AND THE SYSTEM HAD A CHANCE TO "BALANCE OUT" - through years of experience, some of the techs were able to tell if a particular system had enough "juice" or not by just what the stick told them...and usually, after cleaning the fins and compressor out, they'd be within 40-60psi on the high-side and about 0-5psi on the low-side. Experience shows!!!
__________________
.

.
M. G. Burg
'10 - Dakota SXT - Daily Ride / ≈ 172.5K
.'76 - 450SLC - 107.024.12 / < .89.20 K
..'77 - 280E - 123.033.12 / > 128.20 K
...'67 - El Camino - 283ci / > 207.00 K
....'75 - Yamaha - 650XS / < 21.00 K
.....'87 - G20 Sportvan / > 206.00 K
......'85 - 4WINNS 160 I.O. / 140hp
.......'74 - Honda CT70 / Real 125

.
“I didn’t really say everything I said.”
. . . . . . . . . . . . . . . . . . ~ Yogi Berra ~
Reply With Quote
  #3  
Old 01-26-2011, 07:53 PM
420benz's Avatar
Registered User
 
Join Date: Jul 2001
Posts: 961
First:If the fan does not turn then that is the problem.
Second: Remove the side panel and see if the capacitor is swollen,if so replace it. Also check the contactor to see if the contacts are burnt.
Reply With Quote
  #4  
Old 01-26-2011, 08:29 PM
KarTek's Avatar
<- Ryuko of Kill La Kill
 
Join Date: Jun 2007
Location: Bahama/Eno Twp, NC
Posts: 3,258
The unit is definately stalled out. I hear a big buzz every time it tries to start.

So, is the capacitor under a side cover or is it on the compressor?

Thanks for the insight so far. I'll probably get back on it this weekend.
__________________
-Evan


Benz Fleet:
1968 UNIMOG 404.114
1998 E300
2008 E63


Non-Benz Fleet:
1992 Aerostar
1993 MR2
2000 F250
Reply With Quote
  #5  
Old 01-26-2011, 11:13 PM
Registered User
 
Join Date: Mar 2007
Posts: 159
A residential HVAC system with high or low pressure safety switches would be a surprise. A failed run start capacitor would be the first thing to check. If the capacitor is OK. Check the compressor. Remove the cover where the wires are connected to the compressor. Trace the wires to where they are connected to the power relay and capacitor. Carefully observe and mark where they were removed. These will be the run start and common connections. None of these should read to ground. Do not try to remove the wires from the compressor. I only mention this so as not to damage the fusetite terminal assembly. (there is system pressure behind the terminals) Hopefully it is a defective capacitor. The only other device that comes to mind may be a compressor dead headed against a stuck reversing valve. (thats a reach) Allowing the compressor to continually try to start is not a good thing. There is an internal overload inside the compressor. When it cools down and closes the circuit the compressor will try to start. Last but not least check the supply voltage it should be 220v. Good Luck
Reply With Quote
  #6  
Old 01-30-2011, 07:21 PM
KarTek's Avatar
<- Ryuko of Kill La Kill
 
Join Date: Jun 2007
Location: Bahama/Eno Twp, NC
Posts: 3,258
I dug into it today since it was nice outside and here's what I found:

It actually DOES have high and low pressure switches, just like an automotive type system. However, I don't think that's the problem in this case. I pulled the capacitor (it was very to locate and identify) and it was slightly swollen, leaking a clear oil from around the terminals.

I'm ordering a new one and we'll see how that does.
__________________
-Evan


Benz Fleet:
1968 UNIMOG 404.114
1998 E300
2008 E63


Non-Benz Fleet:
1992 Aerostar
1993 MR2
2000 F250
Reply With Quote
  #7  
Old 01-30-2011, 08:05 PM
OMEGAMAN's Avatar
Registered User
 
Join Date: May 2005
Posts: 705
Quote:
Originally Posted by KarTek View Post
I dug into it today since it was nice outside and here's what I found:

It actually DOES have high and low pressure switches, just like an automotive type system. However, I don't think that's the problem in this case. I pulled the capacitor (it was very to locate and identify) and it was slightly swollen, leaking a clear oil from around the terminals.

I'm ordering a new one and we'll see how that does.
If that doesnt do it get your meter out and measure the resistance of the start and run windings. Also there is a way to run motors backwards for a second to un jam them.
Reply With Quote
  #8  
Old 01-30-2011, 08:54 PM
KarTek's Avatar
<- Ryuko of Kill La Kill
 
Join Date: Jun 2007
Location: Bahama/Eno Twp, NC
Posts: 3,258
Cool, thanks.
__________________
-Evan


Benz Fleet:
1968 UNIMOG 404.114
1998 E300
2008 E63


Non-Benz Fleet:
1992 Aerostar
1993 MR2
2000 F250
Reply With Quote
  #9  
Old 01-30-2011, 10:23 PM
Skid Row Joe's Avatar
Banned
 
Join Date: Oct 2007
Location: #KeepingAmericaGreat!
Posts: 7,071
Quote:
Originally Posted by KarTek View Post
Guys, I have a fairly new system for the upstairs - heat pump, R410/puron, scroll compressor. When it was installed, it was supposed to a fairly high end unit.

Well now, about 6 years later, it won't start. When the compressor tries to run, it just buzzes for about 5 seconds then clicks and quits. Then, about 10 seconds later, it does it again and keeps repeating but never gets started.

I can probably figure it out eventually, either the starter capacitor or contactor but if anyone knows for sure, it would sure save me a lot of time.

Thanks for any help you can give!
Do you clean the exterior fins every year?
Reply With Quote
  #10  
Old 01-31-2011, 06:05 AM
KarTek's Avatar
<- Ryuko of Kill La Kill
 
Join Date: Jun 2007
Location: Bahama/Eno Twp, NC
Posts: 3,258
Not really "every year", more like I blow it off every time I'm doing yard work or using the leaf blower. It's pretty clean.
__________________
-Evan


Benz Fleet:
1968 UNIMOG 404.114
1998 E300
2008 E63


Non-Benz Fleet:
1992 Aerostar
1993 MR2
2000 F250
Reply With Quote
  #11  
Old 01-31-2011, 09:51 AM
Registered User
 
Join Date: Feb 2003
Location: Durham, NC
Posts: 158
Check the resistance of the start/run windings.

A common compressor failure is the rotor in the compressor locking up (locked rotor condition), which would cause a hum for 5-10 seconds before the motor windings overheat and are shut down by the internal thermal protector in the compressor. Check the resistance of the run/start windings after the humming stops to determine if it shows an "open" winding which would have been caused by the thermal protector opening the circuit. Heat Pump compressors generally last 10-12 years (average).
Reply With Quote
  #12  
Old 02-06-2011, 07:19 AM
KarTek's Avatar
<- Ryuko of Kill La Kill
 
Join Date: Jun 2007
Location: Bahama/Eno Twp, NC
Posts: 3,258
OK, just to wrap this up. I picked up a new capacitor at ACR on Friday and installed it yesterday. The old one had swollen and the top where the terminals was somewhat dome shaped with a clear, oily liquid oozing from inside.

$7 part and it works like a charm now!

Thanks for the suggestions!
__________________
-Evan


Benz Fleet:
1968 UNIMOG 404.114
1998 E300
2008 E63


Non-Benz Fleet:
1992 Aerostar
1993 MR2
2000 F250
Reply With Quote
  #13  
Old 02-06-2011, 09:15 AM
420benz's Avatar
Registered User
 
Join Date: Jul 2001
Posts: 961
Quote:
Originally Posted by KarTek View Post
OK, just to wrap this up. I picked up a new capacitor at ACR on Friday and installed it yesterday. The old one had swollen and the top where the terminals was somewhat dome shaped with a clear, oily liquid oozing from inside.

$7 part and it works like a charm now!

Thanks for the suggestions!
Ive replaced many of them! That's why i always go for the easy fix.You just saved $$$$$$$$$$. Congratulation.

Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On




All times are GMT -4. The time now is 09:11 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2024 Pelican Parts, LLC - Posts may be archived for display on the Peach Parts or Pelican Parts Website -    DMCA Registered Agent Contact Page