Wiring requirements for MIG welder

I just bought a Lincoln 175 HD MIG welder. My neighbor at my warehouse is a metal fabricator and he confirmed my suspicion that 220 was about the only way to go. My shop has 3 phase power coming into the box, which I don't really need, no circuits wired up at any rate, and only one 220 circuit, for the baseboard heater and it's a 20 amper. I need to put in a dedicated circuit going to the garage part of my shop, 50 feet away.

Lincoln says a 40 amp breaker is required. This would mean 8-2 with ground. I've seen a couple of web sites that claim 10-2 w/G and a 30 amp breaker is more than enough. My neighbor also thought 30 would do it.

Whattyathink?

__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
  #2  
Old 11-12-2007, 04:17 AM
Carleton Hughes's Avatar
Registered User
 
Join Date: Dec 2004
Posts: 1,611
Quote:
Originally Posted by cmac2012 View Post
I just bought a Lincoln 175 HD MIG welder. My neighbor at my warehouse is a metal fabricator and he confirmed my suspicion that 220 was about the only way to go. My shop has 3 phase power coming into the box, which I don't really need, no circuits wired up at any rate, and only one 220 circuit, for the baseboard heater and it's a 20 amper. I need to put in a dedicated circuit going to the garage part of my shop, 50 feet away.

Lincoln says a 40 amp breaker is required. This would mean 8-2 with ground. I've seen a couple of web sites that claim 10-2 w/G and a 30 amp breaker is more than enough. My neighbor also thought 30 would do it.

Whattyathink?
2 110 legs and a neutral Bus,8-3 with ground w/1 30 Murray breaker on each {2} hot legs.Better safe than sorry.
Reply With Quote
  #3  
Old 11-12-2007, 08:14 AM
Registered User
 
Join Date: Aug 2001
Location: Milford, DE
Posts: 1,558
I have a Lincoln 175 TIG setup in my garage that is powered via a 30 amp circuit. According to the owners manual it requires a 70 amp 220 connection to deliver the full 175 amp rating. My setup works fine up until about the 100-110 amp level - then it will blow a circuit breaker. Since I use the machine mainly for fine work (sheet metal) I really don't care about about utilizing the higher end of the amp spectrum - I typically do most of my welding at the 20-40 amp level.

At the 100 amp level I can weld steel up to about a 1/4 inch plate and aluminum up to about 1/8 inch - If you are going to be dealing with materials thicker than this you are most likely going to need a higher amp service rating.
__________________
98 Dodge-Cummins pickup (123k)
13 GLK250 (135k)
06 E320CDI (323K)
16 C300 (62K)
82 300GD Gelaendewagen (54K)
Reply With Quote
  #4  
Old 11-12-2007, 08:59 AM
SwampYankee's Avatar
New England Hick
 
Join Date: Sep 2006
Location: CT
Posts: 1,501
Quote:
Originally Posted by cmac2012 View Post
I just bought a Lincoln 175 HD MIG welder. My neighbor at my warehouse is a metal fabricator and he confirmed my suspicion that 220 was about the only way to go. My shop has 3 phase power coming into the box, which I don't really need, no circuits wired up at any rate, and only one 220 circuit, for the baseboard heater and it's a 20 amper. I need to put in a dedicated circuit going to the garage part of my shop, 50 feet away.

Lincoln says a 40 amp breaker is required. This would mean 8-2 with ground. I've seen a couple of web sites that claim 10-2 w/G and a 30 amp breaker is more than enough. My neighbor also thought 30 would do it.

Whattyathink?
If you have to put in an additional circuit and wire it up any way, why not go 8-2 w/a 40 amp breaker? It never hurts to have more capacity. You'll never regret having "too much" but you might wish you had more if you go with just enough to get by.
__________________

1980 300TD-China Blue/Blue MBTex-2nd Owner, 107K (Alt Blau) OBK #15
'06 Chevy Tahoe Z71 (for the wife & 4 kids, current mule) '03 Honda Odyssey (son #1's ride, reluctantly) '99 GMC Suburban (255K+ miles, semi-retired mule) 21' SeaRay Seville (summer escape pod)
Reply With Quote
  #5  
Old 11-12-2007, 12:04 PM
79-240d-project's Avatar
Registered User
 
Join Date: Oct 2003
Location: Pacific Northwest, Washington State
Posts: 253
Run the largest capacity your main circuit panel will allow! It can be very useful for other things as well.

You can power your house with the garage 220 via a generator set-up.

DO NOT ATTEMPT THIS UNLESS YOU KNOW WHAT YOU ARE DOING!

When I did my garage I went with the largest my house panel would permit.
__________________
79 240D (no name yet) 203K Miles Maple Yellow
98 2500 4x4 HD Dodge 24 Valve Cummins TD
83 Chevy Van (Dead-Trans. shot)
Reply With Quote
  #6  
Old 11-12-2007, 12:12 PM
E150GT's Avatar
I'm a chicken
 
Join Date: Sep 2006
Location: SAN ANTONIO, TEXAS
Posts: 1,148
my electrician buddy says NMB-10/2wg is only good for 25amps. PLus current drain from distances should be taken into consideration too.
__________________
1984 300SD Orient Red/ Palomino
1989 560SEC
2016 Mazda 6 6 speed manual
1995 Ford F-150 reg cab 4.9 5speed manual
Reply With Quote
  #7  
Old 11-12-2007, 03:58 PM
cmac2012's Avatar
Renaissances Dude
 
Join Date: Dec 2004
Location: Redwood City, CA
Posts: 34,168
Quote:
Originally Posted by TimFreeh View Post
I have a Lincoln 175 TIG setup in my garage that is powered via a 30 amp circuit. According to the owners manual it requires a 70 amp 220 connection to deliver the full 175 amp rating. My setup works fine up until about the 100-110 amp level - then it will blow a circuit breaker. Since I use the machine mainly for fine work (sheet metal) I really don't care about about utilizing the higher end of the amp spectrum - I typically do most of my welding at the 20-40 amp level.

At the 100 amp level I can weld steel up to about a 1/4 inch plate and aluminum up to about 1/8 inch - If you are going to be dealing with materials thicker than this you are most likely going to need a higher amp service rating.
That's good info, I was starting to think that maybe going with the minimum would limit me on occasion. I think I'll go with the 8-2 and a 40 amper.
__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
  #8  
Old 11-12-2007, 04:01 PM
cmac2012's Avatar
Renaissances Dude
 
Join Date: Dec 2004
Location: Redwood City, CA
Posts: 34,168
Quote:
Originally Posted by Carleton Hughes View Post
2 110 legs and a neutral Bus,8-3 with ground w/1 30 Murray breaker on each {2} hot legs.Better safe than sorry.
This welder doesn't need a neutral wire, and the box that fits their 220 cord jack, a Nema 6-50, only has terminals for the 2 110 wires and a ground.

On the 2 30 amp breakers, are you sure it's a good idea to have breakers that are rated higher then the wire?
__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
  #9  
Old 11-12-2007, 04:06 PM
cmac2012's Avatar
Renaissances Dude
 
Join Date: Dec 2004
Location: Redwood City, CA
Posts: 34,168
Good advice all around. I found an electric supply place that is getting me 50 ft. of 8-2 w/g for $1.26 a ft. which is a nickel less than Home Despot wanted for 10-2 (?!). I've run into this before -- HD seduces one into thinking that their prices are always lower and they're not.

I'm about 60 to 70% of an electrician -- I'm confident I can do this safely. I turn off the main breaker at the panel, of course, doubly important due to the 3 phase power in that box. The 3rd leg has a black cable feeding it with an orange band around it, the digital tester says it's 201 volts. Ouchy.
__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
  #10  
Old 11-12-2007, 04:09 PM
Registered User
 
Join Date: Oct 2004
Posts: 185
Suggestion

Go over to "weldtalk.com" and you will get good and info u can count on there. A lot of certfied electricians there.

John
Reply With Quote
  #11  
Old 11-12-2007, 04:11 PM
cmac2012's Avatar
Renaissances Dude
 
Join Date: Dec 2004
Location: Redwood City, CA
Posts: 34,168
Hey, good tip.
__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
  #12  
Old 11-12-2007, 04:21 PM
Registered Shadetree
 
Join Date: Aug 2006
Location: Wilmington, NC
Posts: 676
Quote:
Originally Posted by cmac2012 View Post
The 3rd leg has a black cable feeding it with an orange band around it, the digital tester says it's 201 volts. Ouchy.
That's what we electricians refer to as a "high leg." Gives you 208 or 240 (depending on your feeder transformer's output) to neutral. If you meter between it and a 120v leg, you'll still only get the 208 between legs and can utilize such attachment for 240volt equipment. WARNING -- If said equipment has a neutral, it probably has componentry which utilizes 120v, making attachment to the high leg a very risky proposal.

As a licensed master electrician and electrical contractor, I'd recommend that you adhere strictly to the nameplate rating of the equipment and the NEC when implementing your installation.

If you have any specific questions, ask here or PM me.
__________________
____________
1998 E300 +310,000K
1996 E300 +460,000K



Last edited by Bill Ladd; 11-12-2007 at 05:26 PM. Reason: damn split infinitive
Reply With Quote
  #13  
Old 11-13-2007, 01:26 AM
cmac2012's Avatar
Renaissances Dude
 
Join Date: Dec 2004
Location: Redwood City, CA
Posts: 34,168
Hey, that's quite an offer. I'm mostly a carpenter, and speaking of which, do you know the difference between a carpenter and an electrician?

The carpenter wasn't smart enough to be an electrician.

That's not entirely true of course but if I had it to do over again, I'd have put in a decent apprenticeship as a plumber or electrician back when I was young enough to do it. I can do both to some degree but there are gaps in my knowledge.

One thing I do know is that I stay away from that 3rd leg. I have nothing that utilizes that type of power. I understand it can run a seriously powerful motor and save you money on your electric bill while doing it. Maybe I'll find a need to use it someday and if I do, I believe I'll get a real electrician to do run the circuit.
__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
  #14  
Old 11-13-2007, 06:11 PM
cmac2012's Avatar
Renaissances Dude
 
Join Date: Dec 2004
Location: Redwood City, CA
Posts: 34,168
Quote:
Originally Posted by Lux View Post
That's what we electricians refer to as a "high leg." Gives you 208 or 240 (depending on your feeder transformer's output) to neutral. If you meter between it and a 120v leg, you'll still only get the 208 between legs and can utilize such attachment for 240volt equipment. WARNING -- If said equipment has a neutral, it probably has componentry which utilizes 120v, making attachment to the high leg a very risky proposal.

As a licensed master electrician and electrical contractor, I'd recommend that you adhere strictly to the nameplate rating of the equipment and the NEC when implementing your installation.

If you have any specific questions, ask here or PM me.
What was I thinking -- you're right, it's 208. I checked it again at it flicked back and forth between 208 and 209. I knew it wasn't 220 and I had an odd number on my brain.
__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
  #15  
Old 11-13-2007, 06:38 PM
Registered Shadetree
 
Join Date: Aug 2006
Location: Wilmington, NC
Posts: 676
Quote:
Originally Posted by cmac2012 View Post
What was I thinking -- you're right, it's 208. I checked it again at it flicked back and forth between 208 and 209. I knew it wasn't 220 and I had an odd number on my brain.
Actually, I didn't find that number so odd. Voltage will drop the further you are from the feeding transformer (as the wire length increases, so does the resistance). That's why many appliances and machines will operate within a range of voltage -- if I remember correctly, somewhere around 20% below or above the nameplate rating.

__________________
____________
1998 E300 +310,000K
1996 E300 +460,000K


Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On




All times are GMT -4. The time now is 05:24 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2024 Pelican Parts, LLC - Posts may be archived for display on the Peach Parts or Pelican Parts Website -    DMCA Registered Agent Contact Page