Originally Posted by lutzTD View Post
I had trouble with the shraders as well. the first tiem I did the system everything checked out no leaks. after it was all done it leaked down. I found the low side shrader which had my hose on it during the test was leaking after I removed the hose. the second time it charged ok then the expansion valve jammed. im 0 fer 2
When you say everything checked out no leaks... then leaked...
did you check it under pressure with nitrogen/ four oz r22 ?
or did you only check it under vacuum ?
Sometimes it will hold one direction but not the other.. slight movement of an oring can lose all your refrigerant charge.... of course the use of the correct color Nylog really helps too...