Electrical Question

I am going to start building a kid's treehouse/archery deerstand. I am thinking about running electrical to the tree.

I have a breaker box 350-450' feet away. It has at least one empty spot and it was for an inground pool (that no longer exists) and some outdoor lighting.

I am not planning on more than a 15 amp breaker as it will just be a light or two, an outlet and possibly setting up a deer surveillance system.

Any input on the size of wire I need or anything else? I am planning on burying the wire from the outdoor shed (where the breaker box is) to the treehouse.

__________________
2009 ML320 Bluetec
1985 300CD
1981 300TD


Past Mercedes
1979 300TD
1982 300TD
2000 E320 4Matic Wagon
1998 E430
1984 300SD
1980 300SD
Reply With Quote
  #2  
Old 09-04-2013, 04:34 PM
t walgamuth's Avatar
dieselarchitect
 
Join Date: Apr 2005
Location: Lafayette Indiana
Posts: 38,632
Its a long feed but if you are not powering anything like a motor or something affected by a voltage drop the loss from distance will probably just make the bulb dimmer. If it gets too hot it will break the breaker.

I'm not an electrician so those who know more than I will correct as needed.
__________________
[SIGPIC] Diesel loving autocrossing grandpa Architect. 08 Dodge 3/4 ton with Cummins & six speed; I have had about 35 benzes. I have a 39 Studebaker Coupe Express pickup in which I have had installed a 617 turbo and a five speed manual.[SIGPIC]

..I also have a 427 Cobra replica with an aluminum chassis.
Reply With Quote
  #3  
Old 09-04-2013, 04:52 PM
jplinville's Avatar
Conservative
 
Join Date: Sep 2008
Location: Dayton, Ohio region
Posts: 302
I would do this instead...Wire it with an outlet or two, perhaps a light socket, and wire it all to a male lead out of the side wall. This way you can run an extension cord to the old pool outlet when needed. I doubt doing a permanent wire job would pass any sort of legal codes.
__________________
1987 560SL
85,000 miles




Meet on the level, leave on the square. Great words to live by

Were we directed from Washington when to sow and when to reap, we should soon want bread. - Thomas Jefferson: Autobiography, 1821.
Reply With Quote
  #4  
Old 09-04-2013, 04:56 PM
Registered User
 
Join Date: May 2011
Location: NYC
Posts: 6,030
Quote:
Originally Posted by t walgamuth View Post
Its a long feed but if you are not powering anything like a motor or something affected by a voltage drop the loss from distance will probably just make the bulb dimmer. If it gets too hot it will break the breaker.
Breakers don't sense voltage drop, only over-current. As far as voltage drop, just follow the tables for wire thickness over the length of run for the required current and you'll be fine.
Reply With Quote
  #5  
Old 09-04-2013, 05:38 PM
Registered User
 
Join Date: Oct 2012
Posts: 5,924
Use a ground fault breaker for that application if you do it in any fashion like you mention. Reduces the risk to the children.

Or give then something to do by installing 12 volt stuff and a battery charger somewhere for them to charge up some form of battery to power the low voltage system. Led forms of lighting for example will last quite a time on a small motorcycle or lawn tractor battery. Because of the acid risk I would make up a NiCad pack for recharging over an acid based battery.
Reply With Quote
  #6  
Old 09-04-2013, 08:17 PM
Admiral-Third World Fleet
 
Join Date: Feb 2002
Location: Central FL
Posts: 3,069
In this part of the country (lightning capital of the universe) I would get the shivers from any of those wired suggestions. I would use something like Barry's suggestion or a local solar panel. But MN isn't FL

Years ago, when we built the house I put in a long run of wire and water pipe out to the "back 40". Hooked up the water, but never got around to the electricity. A few years later , a tree that it passed by was struck. Blew up the pipe and fried the wire. Thankfully my procrastination saved the day. The wire is still there, in pieces...
__________________
80 300SD (129k mi) 82 240D stick (193k mi)77 240D auto - stick to be (153k mi) 85 380SL (145k mi) 89 BMW 535i 82 Diesel Rabbit Pickup (374k mi) 91 Jetta IDI Diesel (155k mi) 81 VW Rabbit Convertible Diesel 70 Triumph Spitfire Mk III (63kmi)66 Triumph TR4a IRS (90k mi)67 Ford F-100 (??)

Last edited by rs899; 09-05-2013 at 02:59 PM.
Reply With Quote
  #7  
Old 09-04-2013, 09:44 PM
t walgamuth's Avatar
dieselarchitect
 
Join Date: Apr 2005
Location: Lafayette Indiana
Posts: 38,632
Quote:
Originally Posted by barry12345 View Post
Use a ground fault breaker for that application if you do it in any fashion like you mention. Reduces the risk to the children.

Or give then something to do by installing 12 volt stuff and a battery charger somewhere for them to charge up some form of battery to power the low voltage system. Led forms of lighting for example will last quite a time on a small motorcycle or lawn tractor battery. Because of the acid risk I would make up a NiCad pack for recharging over an acid based battery.
This makes much more sense.
__________________
[SIGPIC] Diesel loving autocrossing grandpa Architect. 08 Dodge 3/4 ton with Cummins & six speed; I have had about 35 benzes. I have a 39 Studebaker Coupe Express pickup in which I have had installed a 617 turbo and a five speed manual.[SIGPIC]

..I also have a 427 Cobra replica with an aluminum chassis.
Reply With Quote
  #8  
Old 09-04-2013, 10:08 PM
Mölyapina's Avatar
User title not in use
 
Join Date: Oct 2012
Location: Chelmsford, Massachusetts
Posts: 4,373
So are the kids your excuse to put up a deer stand, or will this be genuinely multi-purpose ?
__________________
"Senior Luna, your sense of humor is still loco... but we love it, anyway." -rickymay ____ "Your sense of humor is still loco... " -MBeige ____ "Señor Luna, your sense of humor is quite järjetön" -Delibes

1982 300SD -- 211k, Texas car, tranny issues ____ 1979 240D 4-speed 234k -- turbo and tuned IP, third world taxi hot rod

2 Samuel 12:13: "David said to Nathan, “I have sinned against the Lord.” And Nathan said to David, “The Lord also has put away your sin; you shall not die."
Reply With Quote
  #9  
Old 09-04-2013, 11:34 PM
I miss my MBZ
 
Join Date: Feb 2003
Location: Cincinnati, OH
Posts: 563
the closest wire size calculator I can find (Electrician Continuing Education) says to use 10awg - I said that the run was 500ft. 10awg should also supply you well if you put an outlet and ever want to plug in something big (fan, power tools, space heater etc...) - you know that you will

look for "outdoor" and "direct bury" ratings on things- they should last longer.

And know that you are indeed rednecking this, be careful as the years go on, keep your eye on the terminations etc...

Mike Holt Enterprises Home - real electricians hang out there, if you want some better advice

-John
__________________
2009 Kia Sedona
2009 Honda Odyssey EX-L
12006 Jetta Pumpe Duse
(insert Mercedes here)

Husband, Father, sometimes friend =)
Reply With Quote
  #10  
Old 09-04-2013, 11:41 PM
Registered User
 
Join Date: Mar 2006
Posts: 1,392
minnesota.yes it's for deer!kids come second.from what i have heard for every 100 ft you need to drop a gauge.but your not running much for power so i would say 10 gauge should do ya.go rent a trencher and you can have it trenched in a couple hours or so.BUT be sure to have a locate done to check for any underground gas lines,electric,etc.it is the law no matter where you live.and believe me you DO NOT want to hit a fiber optic cable.buddy hit one about 10 yrs ago and is still paying for it.
Reply With Quote
  #11  
Old 09-05-2013, 08:08 AM
Registered User
 
Join Date: Dec 2005
Location: Carson City, NV
Posts: 3,851
Quote:
Originally Posted by barry12345 View Post
Use a ground fault breaker for that application if you do it in any fashion like you mention. Reduces the risk to the children.

Or give then something to do by installing 12 volt stuff and a battery charger somewhere for them to charge up some form of battery to power the low voltage system. Led forms of lighting for example will last quite a time on a small motorcycle or lawn tractor battery. Because of the acid risk I would make up a NiCad pack for recharging over an acid based battery.
THIS!

And check code before you do anything. If you do go with wired power definitely use a GFCI even if code doesn't require it. You don't want you or yours to become crispy critters.
__________________
Whoever said there's nothing more expensive than a cheap Mercedes never had a cheap Jaguar.

83 300D Turbo with manual conversion, early W126 vented front rotors and H4 headlights 400,xxx miles
08 Suzuki GSX-R600 M4 Slip-on 22,xxx miles
88 Jaguar XJS V12 94,xxx miles. Work in progress.
Reply With Quote
  #12  
Old 09-05-2013, 02:24 PM
Graplr's Avatar
Registered User
 
Join Date: Apr 2007
Location: Huntington Beach, CA
Posts: 1,649
Thanks for all the replies.

First, yes it is a true multifunctional purpose of kids and deer hunting. I have been promising my 7 year old a tree house for a few years and I want to build a better stand so 2 in 1. He does come sit with me sometimes when I go hunting in the back yard so it would be both anyways! Right?

Second, solar is out as it is in a well forested area. I don't want to deal with a battery, the whole point is to make something permanent.

Third, I was planning on renting a trencher. I already know where the underground stuff is. I had geothermal put in two years ago. I am a bit rural so I don't have much. Definitely will use a GFCI outlet. I paced it off and got 163 paces. I figure about 2.5 feet per pace so that puts it at just over 400' which sounds about right. I figured 10 gauge would handle it but I just wanted to be certain I couldn't use a lower gauge. I will head over to the suggested forum.
__________________
2009 ML320 Bluetec
1985 300CD
1981 300TD


Past Mercedes
1979 300TD
1982 300TD
2000 E320 4Matic Wagon
1998 E430
1984 300SD
1980 300SD
Reply With Quote
  #13  
Old 09-05-2013, 02:48 PM
Banned
 
Join Date: May 2004
Location: Varies
Posts: 4,802
Multiple smaller wires are sometimes cheaper than a singular heavy wire. It is something to think about if you find a great deal, improvise.

If you hook in an RV receptacle you might later find it useful.

Any chance you might put a future outbuilding along the line?

What else might be useful in that trench?
Reply With Quote
  #14  
Old 09-06-2013, 12:12 AM
Banned
 
Join Date: May 2002
Location: Blue Point, NY
Posts: 25,396
Quote:
Originally Posted by Graplr View Post
I figured 10 gauge would handle it but I just wanted to be certain I couldn't use a lower gauge. I will head over to the suggested forum.
400 feet of 10 gauge UF is going to cost you a fortune (almost $500.).

Are you sure you need 15 amps............reducing that number a bit would allow you to go down to 12 guage............quite a bit of a saving.

It all depends what you intend to run in the tree house.
Reply With Quote
  #15  
Old 09-06-2013, 02:44 AM
cmac2012's Avatar
Renaissances Dude
 
Join Date: Dec 2004
Location: Redwood City, CA
Posts: 34,108
I had a thought to run 12 volt. Could have some batteries staying topped off so you could have more amperage when you want it. 14 gauge would probably work for that. Less health hazard. Could also have a small solar panel keeping them topped off during sunny periods. I had friends in the hills who used 12 volt lights and appliances back when - just dispensed with the whole inverter thing which saps energy. I'd bet there's still a good market for those things.

__________________
1986 300SDL, 362K
1984 300D, 138K
Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On




All times are GMT -4. The time now is 05:56 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2024 Pelican Parts, LLC - Posts may be archived for display on the Peach Parts or Pelican Parts Website -    DMCA Registered Agent Contact Page